Although it’s true that the work in this case wasn’t done to specification, it seems it’s also true that the specification wasn’t safe either.
the original design of the rod hanger connection would have supported 90 kN, only 60% of the 151 kN required by the Kansas City building code. Even if the details had not been modified the rod hanger connection would have violated building standards.